CuriousElectron
Electrical
- Jun 24, 2017
- 186
Greetings,
I've got a distribution system which is getting upgraded to add a manual transfer switch with a back-up source. The caveat is that the MTS will be switching between Delta-Delta transformers with center tap on the secondary of both transformers grounded to provide 120/240, 3 phase, 4 wire service. The utility is feeding the MTS via a step-down transformer with circuit breaker on the load side for protection for the MTS. The alternate source is standby gen. feeding the MTS via a step-up xfmr.
Should I use 3-4 pole circuit breaker upstream of the MTS? There is no ground protection scheme.
I'm thinking solid neutral at the MTS and 3-pole breaker is fine, since I don't have any ground CTs. My only concerns is that you could treat the two power sources as separately derived sources, since both sources are feeding MTS via grounded delta transformers.
Thoughts?
EE
I've got a distribution system which is getting upgraded to add a manual transfer switch with a back-up source. The caveat is that the MTS will be switching between Delta-Delta transformers with center tap on the secondary of both transformers grounded to provide 120/240, 3 phase, 4 wire service. The utility is feeding the MTS via a step-down transformer with circuit breaker on the load side for protection for the MTS. The alternate source is standby gen. feeding the MTS via a step-up xfmr.
Should I use 3-4 pole circuit breaker upstream of the MTS? There is no ground protection scheme.
I'm thinking solid neutral at the MTS and 3-pole breaker is fine, since I don't have any ground CTs. My only concerns is that you could treat the two power sources as separately derived sources, since both sources are feeding MTS via grounded delta transformers.
Thoughts?
EE