tumbleweed1
Electrical
- Sep 19, 2013
- 44
We have a 4160V to 600V Delta (primary) Wye (secondary) transformer, 1.5MVA.
I had planned to simply ground the neutral on the secondary wye side as the load bank does not require line-neutral load. I understand that this poses a risk for excessive ground fault current to flow.
We have a zero sequence CT on the feeder. Would this mitigate the risk/minimize the time that a ground fault could occur?
I had planned to simply ground the neutral on the secondary wye side as the load bank does not require line-neutral load. I understand that this poses a risk for excessive ground fault current to flow.
We have a zero sequence CT on the feeder. Would this mitigate the risk/minimize the time that a ground fault could occur?