aolalde
Electrical
- Dec 16, 2003
- 1,022
In a cruise ship, 5 identical synchronous generators are connected in parallel sharing the total load.
One generator failed to ground. Preliminary testing, with Megger and feeding AC to the fault shows one grounded spot on phase 2,
Generator Name Plate Data: 14000 kVA, 6600 V, 1224.7 Amps, 60 Hz, 514.3 rpm, ODP, PF 0.80
Stator Winding: 126 slots, 126 coils lap, 42 groups of 3 coil each, 7 circuits Wye
TPC 21, coil span 1-7, six terminal leads.
Since removal of this generator from the ship is very expensive and time consuming, the owner wants to clear the ground and work the generator with the coil or coils grounded cut out of the winding (capped).
Is this possible? Assuming a single coil is grounded what is the best way to clear that ground fault?
Should it develop dangerous internal circulating currents?
Have any one solved a similar problem? Many thanks in advance for your comments.
One generator failed to ground. Preliminary testing, with Megger and feeding AC to the fault shows one grounded spot on phase 2,
Generator Name Plate Data: 14000 kVA, 6600 V, 1224.7 Amps, 60 Hz, 514.3 rpm, ODP, PF 0.80
Stator Winding: 126 slots, 126 coils lap, 42 groups of 3 coil each, 7 circuits Wye
TPC 21, coil span 1-7, six terminal leads.
Since removal of this generator from the ship is very expensive and time consuming, the owner wants to clear the ground and work the generator with the coil or coils grounded cut out of the winding (capped).
Is this possible? Assuming a single coil is grounded what is the best way to clear that ground fault?
Should it develop dangerous internal circulating currents?
Have any one solved a similar problem? Many thanks in advance for your comments.