Mbrooke
Electrical
- Nov 12, 2012
- 2,546
Why is grounding the neutral at the transformer and generator forbidden? I can't see any reason for this as the neutral will not be carrying load current and thus no objectionable current would be present.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
In addition there are often different wiring methods for a neutral conductor versus a grounding conductor.waross 14 Dec 19 17:02 said:When a protection scheme includes Ground Fault Current monitoring, all of the normal neutral current must return on the neutral conductor. Any shared neutral current returning on the grounding system will be interpreted as a ground fault current and cause a trip.
Another possible issue is the effect of current passing from one grounding electrode to another grounding electrode.
There have been cases where a current passing through the ground has dried out the soil and caused the resistance to ground to rise above acceptable limits.