In addition there are often different wiring methods for a neutral conductor versus a grounding conductor.waross 14 Dec 19 17:02 said:When a protection scheme includes Ground Fault Current monitoring, all of the normal neutral current must return on the neutral conductor. Any shared neutral current returning on the grounding system will be interpreted as a ground fault current and cause a trip.
Another possible issue is the effect of current passing from one grounding electrode to another grounding electrode.
There have been cases where a current passing through the ground has dried out the soil and caused the resistance to ground to rise above acceptable limits.