Hello,
First the background, then the question.
My system configuration is a 4160V, 2980 kW generator, impedance grounded that outputs to a 4160 - 44kV transformer in a open wye to delta configuration.
Next to this transformer is a distribution substation that feeds town distribution at 4160 V, grounded wye.
The question has come up is: Can we disconnect the distribution sub from its current source, ground the open wye from the generator and feed the distribution circuits from transformer with the generator still able to generate?
Is there damaging currents from grounding that open wye on a impedance grounded generator?
Thank you
First the background, then the question.
My system configuration is a 4160V, 2980 kW generator, impedance grounded that outputs to a 4160 - 44kV transformer in a open wye to delta configuration.
Next to this transformer is a distribution substation that feeds town distribution at 4160 V, grounded wye.
The question has come up is: Can we disconnect the distribution sub from its current source, ground the open wye from the generator and feed the distribution circuits from transformer with the generator still able to generate?
Is there damaging currents from grounding that open wye on a impedance grounded generator?