Grounding an ungrounded Delta-Delta distribution transformer

Status
Not open for further replies.

power2engineer

Electrical
May 18, 2003
53
thread238-262723
I just ran into this NOT so desirable 3750KVA, 34.5KV/480V Delta-Delta transformer. I have attached the transformer Nameplate and 480V Main switchboard Photos.
The Main Switchboard has A voltmeter with Voltage Selector switch which read 480V. In addition it has 3 separate voltmeters marked "Ground Voltmeter #1, #2 and #3 respectively They all read 277V.

1) I am wondering if the system is grounded in a way Mr.David Beach in the referenced thread 238-262723 indicated on 12 Jan 2010 using a WYE (Neutral grounded)-delta Instrument PT for the Ground voltmeters OR can the Instrument PTs be connected using DELTA-Wye (Neutral grounded) to read 277 Phase to neutral

2) How to size this Delta-Wye or Wye Delta transformer for Phase ground fault monitoring voltmeters or for providing system grounding on 480V side?

3) Can this i) Delta-wye or ii) WYE delta solidly grounded neutral be used for all secondary loads requiring neutral / ground connections?

4) In case of WYE-Delta connected grounding transformer the Ground Voltmeters could be connected to each Phase to Neutral and the secondary Delta should be left not connected Open circuit or form at least a delta of its secondary winding?

5) What would be the right way to ground the Main ungrounded Delta-Delta transformer A) by connecting Wye (with solidly grounded neutral) to 480V secondary terminals of Main power transformer or B) by connecting Delta-Wye PTs Delta to the 480V Secondary terminals of the main transformer and using Wye with solidly grounded neutral for Ground detection voltmeters??
 
Replies continue below

Recommended for you

If you have voltmeters measuring phase-neutral voltages of 277 V, you most likely have a grounding transformer on the system. It could be either wye-delta or zig-zag.
 