cmelguet
Electrical
- Jul 19, 2009
- 64
Hi,
I have a grounding question again. Please refer to the attached drawing.
At the project we have an overland conveyor of 1km long. At the start of the conveyor we have a 33/4.16 kV 5 MVA transformer substation with its grounding grid designed according to IEEE 80. At the end of the conveyor we have another substation of 33/4.16 kV 5 MVA, again with its grounding grid designed according to IEEE 80. Between the two grounding grids there are 2 naked copper conductors of 4/0 AWG, buried at 600 mm depth, to connect both grounding grids and to earth the conveyor structure (equipotencial bonding). Since we have a lot of rock where the conveyor is located, the construction company is not able to buried the 2 copper conductors.
The conveyor also have a cable ladder installed with a 2/0 AWG naked copper conductor, used as a grounding conductor for the cable ladder. This conductor is only connected to the grounding grid at the start and end points of the conveyor. (red mark on the drawing).
My suggestion is to eliminate the 2 buried copper conductors and use the cable ladder copper conductor to bond the conveyor structure. Is this acceptable by the NEC? From my understanding the 2 buried conductors are used only for equipotencial bonding and not for step and touch voltage control.
Please your comments.
Regards.
Cmelguet
I have a grounding question again. Please refer to the attached drawing.
At the project we have an overland conveyor of 1km long. At the start of the conveyor we have a 33/4.16 kV 5 MVA transformer substation with its grounding grid designed according to IEEE 80. At the end of the conveyor we have another substation of 33/4.16 kV 5 MVA, again with its grounding grid designed according to IEEE 80. Between the two grounding grids there are 2 naked copper conductors of 4/0 AWG, buried at 600 mm depth, to connect both grounding grids and to earth the conveyor structure (equipotencial bonding). Since we have a lot of rock where the conveyor is located, the construction company is not able to buried the 2 copper conductors.
The conveyor also have a cable ladder installed with a 2/0 AWG naked copper conductor, used as a grounding conductor for the cable ladder. This conductor is only connected to the grounding grid at the start and end points of the conveyor. (red mark on the drawing).
My suggestion is to eliminate the 2 buried copper conductors and use the cable ladder copper conductor to bond the conveyor structure. Is this acceptable by the NEC? From my understanding the 2 buried conductors are used only for equipotencial bonding and not for step and touch voltage control.
Please your comments.
Regards.
Cmelguet