stevenal
Electrical
- Aug 20, 2001
- 3,823
I am learning from our metermen that electricians are not always providing bonding when using PVC between CT cans and meter bases. Seems the inspectors are content to leave this in the utility (our) domain. Our metermen are then using the CT secondary neutrals to provide this bonding path. I am making my displeasure with this practice known since we run the risk of creating current loops if an unobserved bond is present, or if one is added later. I wish to make it a requirement that proper bonding be provided prior to our guys wiring the secondaries. The question is then, what size bonding wire to require? NEC speaks of sizing based on overcurrent protection when installed after the service, and based on service conductor size when installed before. But no service conductors run through the meter base, and the instrument transformers have no overcurrent protection. We use #12 for potentials and #10 for currents, so I'm proposing #8 for the bond on the theory that any wire supplying a fault will burn apart prior to the bond wire. Reasonable? Code compliant? Thanks.