mb3928
Electrical
- May 27, 2020
- 26
For a typical large-scale lithium ion battery energy storage system, a battery container may have a rating of 5 MWh usable, 2 MW DC continuous discharge power, with a nominal 1000V DC bus voltage ranging from 700V-1100V DC in service. DC fault current can be as high as 200 kA. The DC system is ungrounded and incorporates fusing on both poles as well as GFD / insulation monitoring.
I am wondering if anyone has any insight into design criteria for the premises grounding system & equipment grounding connections - neither the manufacturer nor IEEE literature seems to have much guidance on grounding design for high DC fault current sources. Should I be designing for a multiple ground fault scenario? Do I need to worry about touch voltages in the event of multiple ground faults? Is that overkill given it's an ungrounded system? Any input is appreciated.
I am wondering if anyone has any insight into design criteria for the premises grounding system & equipment grounding connections - neither the manufacturer nor IEEE literature seems to have much guidance on grounding design for high DC fault current sources. Should I be designing for a multiple ground fault scenario? Do I need to worry about touch voltages in the event of multiple ground faults? Is that overkill given it's an ungrounded system? Any input is appreciated.