dougjl
Electrical
- Sep 14, 2001
- 44
NEC code 250.66 discusses the minimum sizing for the grounding electrode conductors. It shows that the largest size required as 3/0 when the area of the incoming service conductors exceed 1100 kcmil. 250.66(A) shows the minimum size for connecting ground rods, pipe & plates as 6 AWG. 250.66(B) shows the minimum size to be used when connecting to the foundation rebar as no less than 4 AWG.
I have seen several different facilities where all of the grounding of those items is done with bare 4/0 copper. I was curious if this is just a "tradition" or if there was a different code I have missed. I realize that code is calling out the minimum sizes and that nothing prevents me from using larger wire, but the cost of copper being what it is I want to make sure that extra expense has validity.
I have also seen a drawing for a new building construction that shows a 4/0 bare copper cable connecting via cadweld to a ground rod. And then shows a #6 jumper jumping between the 4/0 conductor and the ground rod (also connect via cadweld). That doesn't make sense to me. Is there a code reason for this?
Thanks for any input,
Doug
I have seen several different facilities where all of the grounding of those items is done with bare 4/0 copper. I was curious if this is just a "tradition" or if there was a different code I have missed. I realize that code is calling out the minimum sizes and that nothing prevents me from using larger wire, but the cost of copper being what it is I want to make sure that extra expense has validity.
I have also seen a drawing for a new building construction that shows a 4/0 bare copper cable connecting via cadweld to a ground rod. And then shows a #6 jumper jumping between the 4/0 conductor and the ground rod (also connect via cadweld). That doesn't make sense to me. Is there a code reason for this?
Thanks for any input,