A marina floating dock with a large 1-phase transformer is being fed from shore two multiconductor cables each of which incorporates 4-#1 bare ground conductors (83,690CM each). The transformer secondary neutral must connect to an electrode grounding wire that in this case must be sized as the equivalent of a 3/0 cable (167,800CM). The 4-#1 ground conductors in one multiconductor cable total almost 335,000CM when they are paralleled, and would be more than suitable for a system grounding electrode conductor, sizewise. However, the NEC rule for paralleling conductors states that conductors cannot be paralleled if smaller than 1/0 which seems to rule out using the #1 ground conductors in the cable as grounding electrode conductors. Are there any exceptions to this rule and what is it based on? It doesn't seem logical if all of the paralleled conductors are exactly the same size and length in one common cable.
Any help would be appreciated.
Charlie
Any help would be appreciated.