Hi,
I have just found this great forum and had to register immediately.
I have a theoretical problem at hand concerning parallel medium voltage generators prime feeding the grid.
I have drawn up a fictional network of five gen sets connected to a 10kV switchboard. In order to try to understand things involved. The switchboard is connected to a 16MVA delta-wye transformer, stepping the voltage up to 110kV.
What confuses me is the relation between transformer and generator sets grounding. If the transformer would be connected to a stable 110kV grid the star point could be grounded or not (if not, then maybe simply just having a over voltage protection to ground from the star point)
I have understood that if having the star points ungrounded at the generators, and if a phase to ground fault at e.g the generator switchboard then there would be serious difference between phase voltages from the gen sets. Lowering the voltage at the faulty phase and higher voltages for the remainig two phases.
And if assumed a very small resistance for the ground fault, close to zero, then the voltage would totally collapse on the faulty phase and cause the main voltage 10kV as phase voltage on the healthy phases.
If solidly grounding, or low resistance grounding, the generator star points then a phase to ground fault would cause seriously high ground currents. Maybe damaging the generator windings, although having protection relays for the gen sets. I have understood that there could also be problems with third harmonic currents during normal operation.
If using high resistance grounding for each gen set then the phase to ground current would be lower and maybe allowing some delay to be set in the protection unit, without compromising the generators. But what would happen concerning the selectivity between generator- and main transformer circuit breakers?
Seems that I have stumbled over this grounding issue, and I would appreciate if someone could kick my brain regarding correct choice of grounding. And would You have any information regarding how the resistance of the neutral grounding resistor is chosen?
I have just found this great forum and had to register immediately.
I have a theoretical problem at hand concerning parallel medium voltage generators prime feeding the grid.
I have drawn up a fictional network of five gen sets connected to a 10kV switchboard. In order to try to understand things involved. The switchboard is connected to a 16MVA delta-wye transformer, stepping the voltage up to 110kV.
What confuses me is the relation between transformer and generator sets grounding. If the transformer would be connected to a stable 110kV grid the star point could be grounded or not (if not, then maybe simply just having a over voltage protection to ground from the star point)
I have understood that if having the star points ungrounded at the generators, and if a phase to ground fault at e.g the generator switchboard then there would be serious difference between phase voltages from the gen sets. Lowering the voltage at the faulty phase and higher voltages for the remainig two phases.
And if assumed a very small resistance for the ground fault, close to zero, then the voltage would totally collapse on the faulty phase and cause the main voltage 10kV as phase voltage on the healthy phases.
If solidly grounding, or low resistance grounding, the generator star points then a phase to ground fault would cause seriously high ground currents. Maybe damaging the generator windings, although having protection relays for the gen sets. I have understood that there could also be problems with third harmonic currents during normal operation.
If using high resistance grounding for each gen set then the phase to ground current would be lower and maybe allowing some delay to be set in the protection unit, without compromising the generators. But what would happen concerning the selectivity between generator- and main transformer circuit breakers?
Seems that I have stumbled over this grounding issue, and I would appreciate if someone could kick my brain regarding correct choice of grounding. And would You have any information regarding how the resistance of the neutral grounding resistor is chosen?