We have a substation with a 110/11kv , 10 MVA ynyn transformer and 11kv feeders from the l.v side of the transformer. In the same substation compound, we have a 11/0.44kv dyn transformer for auxiliary purposes. Can we connect the neutral on the 0.44kv side of the transformer to earthmat where 11kv side neutral of the 110/11kv transformer is grounded? Some say 0.44kv side neutral should be grounded seperately and should not be connected to 11kv side neutral grounding earthmat. Is this correct? If correct, what is the reason? I request your valuable comments.
With regards.
appunni
We have a substation with a 110/11kv , 10 MVA ynyn transformer and 11kv feeders from the l.v side of the transformer. In the same substation compound, we have a 11/0.44kv dyn transformer for auxiliary purposes. Can we connect the neutral on the 0.44kv side of the transformer to earthmat where 11kv side neutral of the 110/11kv transformer is grounded? Some say 0.44kv side neutral should be grounded seperately and should not be connected to 11kv side neutral grounding earthmat. Is this correct? If correct, what is the reason? I request your valuable comments.