bdn2004

Electrical
Jan 27, 2007
799
We are installing a new pre-fab electrical building on a new foundation. The engineering firm puts on the drawing to bond the rebar to the grounding system. Does the rebar have to be bonded in any certain way?
 
Replies continue below

Recommended for you

There are UL-approved connectors for this application. The best is to use exothermic weld (Cadweld), but there are approved compression fittings as well. Burndy makes a wide range of compression fittings for direct-buried grounding applications. Cadweld and/or Burndy will be able to help you.

 