Hi,
I have to design the grounding system of a power plant. Soil resistivity report shows maximum value or 1571 Ohm-cm. I have a query that whether a less than 2 ohm resistance is essentially required for a single rod burried isolated with the system or it is a requirement of total grounding network? Please give the exact reference for this. If single rod resistivity should be less than 2 ohm, then a 9 meter rod is required to fulfill the condition which is impracticable at site. I have gone through IEEE 80 but couldn't found specific value for that. Please clarify.
I have to design the grounding system of a power plant. Soil resistivity report shows maximum value or 1571 Ohm-cm. I have a query that whether a less than 2 ohm resistance is essentially required for a single rod burried isolated with the system or it is a requirement of total grounding network? Please give the exact reference for this. If single rod resistivity should be less than 2 ohm, then a 9 meter rod is required to fulfill the condition which is impracticable at site. I have gone through IEEE 80 but couldn't found specific value for that. Please clarify.