electricpete
Electrical
- May 4, 2001
- 16,774
We have a group of outdoor motors located outdoors and remote from our main plant.
We have noticed a dramatically higher winding failure rate on these remote outdoor motors than on our remaining motors which are indoors and at our plant. Many of the failures occur during rain and lightning storms. Most of the failures were phase to ground and a few phase to phase. None showed evidence of turn to turn damage except for phase failures where damage could not be distinguished Some line-end coils, some middle coils, some end-turn, some slot. (total of about 12 failures over 12 years.... sorry I can't describe them all).
We have focused on what appears to be the obvious cause: outdoor environment and possible moisture intrusion.
Someone raised another possible consideration. There is a strongly interconnected ground grid below the main plant. All transformers and generators are tied directly to this grid. However the remote outdoor area with the high-failure-rate motors is expected to have a weaker connection to the main ground grid. (we haven’t done any ground system measurements).
The motors are ug-wye connected. The systems are 13.2kv low-resistance grounded w surge caps at motors and 4kv high-resistance grounded (no surge caps at motors). This is the same system that feeds the plant motors (low-failure rate). Switchgear is all located in the plant and cables feeding these outdoor motors are ~200 meters.
Would you think based on the above there might be some considerations associated with the grounding system (or power system) that could contribute to the higher failure rate of the remote motors?
We have noticed a dramatically higher winding failure rate on these remote outdoor motors than on our remaining motors which are indoors and at our plant. Many of the failures occur during rain and lightning storms. Most of the failures were phase to ground and a few phase to phase. None showed evidence of turn to turn damage except for phase failures where damage could not be distinguished Some line-end coils, some middle coils, some end-turn, some slot. (total of about 12 failures over 12 years.... sorry I can't describe them all).
We have focused on what appears to be the obvious cause: outdoor environment and possible moisture intrusion.
Someone raised another possible consideration. There is a strongly interconnected ground grid below the main plant. All transformers and generators are tied directly to this grid. However the remote outdoor area with the high-failure-rate motors is expected to have a weaker connection to the main ground grid. (we haven’t done any ground system measurements).
The motors are ug-wye connected. The systems are 13.2kv low-resistance grounded w surge caps at motors and 4kv high-resistance grounded (no surge caps at motors). This is the same system that feeds the plant motors (low-failure rate). Switchgear is all located in the plant and cables feeding these outdoor motors are ~200 meters.
Would you think based on the above there might be some considerations associated with the grounding system (or power system) that could contribute to the higher failure rate of the remote motors?