Grounding Transformer and building

Status
Not open for further replies.

Eclair

Electrical
Oct 14, 2007
12
US
Hi guys

Here is the situation:
I have to ground an old 2 floor building and a new 1.5MVA transformer located behind.

Here is what I would do for the transformer:
-Belt the transfomer with a bare 4/0 copper cable.
-Ground the metal structure of the enforced concrete structure surrounding the transfomer and below the tranformer.
-Ground the metal barrier.
-Ground all this with four 10'x 3/4" copper rods at the four corner of the transformer (each one at 20' distance from another as per IEEE).
-Connect everything with 4/0 bare copper cable.

For the building:
-Surround the building with a 4/0 bare copper cable at 18" of depth with 10'x 3/4" copper rods at the four corner.
-Connect the building with the grounding system of the transformer at 2 location.

I would like to have some guidelines from you guys cause I can't find anything really useful.

I particulary need:
-depth of stone (rock) to protect the surrounding area of the transformer
-The recommanded area of ground carpet around the tranformer.

I have consulted the IEEE green book for this. It doesn't contain a lot of very useful information.

Thanks
 
Replies continue below

Recommended for you

I would also ground each steel beam of the building structure as well...
 
Make sure thieves can't steal any of it. I'm serious! You need to include that in any design now.

Just had a bunch of cable stolen.

Keith Cress
Flamin Systems, Inc.-
 