grounding vs lightning 1

Status
Not open for further replies.

bshamad

Electrical
Jul 31, 2010
7
AE
we are installing 130 kW motors on a roof top of cooling plant . these motors are fed from VFDs that are contained in MCC panel. We connected earthing cable (yellow/green) from the MCC earthing busbar to each motor body. should we connect the lightning grid on the roof to the motors. i am afraid this will drive the lightning strike into the electrical system!
 
Replies continue below

Recommended for you

No. Keep the down conductors separate from the equipment grounding conductors.

Your lightning arrester rods need to be higher than your motors.