techcrete
Materials
- Feb 9, 2009
- 5
The following scenario lead me to my eventual question:
A field technician is casting C-1107 hydraulic cement non-shrink grout specimens into 2X4 cylinder molds for compressive strength testing..(I have only used 2X4 molds for desktop pencil holders but I digress). The breaks are coming up extremely low. I am aware this is non-compliant with C-1107 & the designated C-109, The field tech's certification status is irrelevant to my forthcoming question. I believe I am in need of some engineering assistance please.
What is the correlation &/or significance of the specimen size, shape, & ratio for casting cubes (1:1) as opposed to cylinders (2:1)? Other than compositional differences between concrete and grouts why couldn't a 2X4 'grout' cylinder be accepted in place of a 2X2 cube? Any help would be greatly appreciated. Thank you in advance for your expertise.
A field technician is casting C-1107 hydraulic cement non-shrink grout specimens into 2X4 cylinder molds for compressive strength testing..(I have only used 2X4 molds for desktop pencil holders but I digress). The breaks are coming up extremely low. I am aware this is non-compliant with C-1107 & the designated C-109, The field tech's certification status is irrelevant to my forthcoming question. I believe I am in need of some engineering assistance please.
What is the correlation &/or significance of the specimen size, shape, & ratio for casting cubes (1:1) as opposed to cylinders (2:1)? Other than compositional differences between concrete and grouts why couldn't a 2X4 'grout' cylinder be accepted in place of a 2X2 cube? Any help would be greatly appreciated. Thank you in advance for your expertise.