Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

gruond fault ct's

Status
Not open for further replies.

Scott0814

Electrical
Apr 29, 2014
1
Hi,
I have a very unusaul qeustion, We haveground fault ct's that are monitoring a panel from one transformer and wired to another panel off of a second transformer, is this going to work as you have a different voltage source you from the amprage you are trying to monitor.r seen this and I am not sure about it working.
 
Replies continue below

Recommended for you

Transformers will transformer current as well as amperage. Interposing transformers are used to match the CTs with the monitoring instrument or relay.
If the CT secondary is rated at 5 Amps and the monitoring device wants an input of 1 amp, then a 5:1 Amp CT may be interposed to effect an efficient match.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor