Gwhiz
Electrical
- Nov 30, 2001
- 3
I am upgrading the relaying at one of our generating stations from the old GE BDD15 to a pair of new Beckwith M-3310 relays. I want to take advantage of its features other than differential.
The transformer is rated at 145MVA 14.4/69 kV and connected in a delta wye configuration.
The generator is rated at 160MVA 15kV.
The two are connected in a unit configuration with two unit auxiliary transformers.
Question #1: In trying to set backup overcurrent relaying, I have found it difficult to coordinate with the inrush current curve. I have plotted the relay curves, transformer damage curve and inrush curve on a graph using Excel. The values for the inrush curve come from the Electrical Distribution System Protection book by Cooper. In reviewing relay settings for the same type of relay at another of our generating stations, I noticed that parts of the backup overcurrent curve specified for that relay lie to the left of the inrush curve for that transformer. (Similar configuration, transformer rated at 231 MVA) Are there any special considerations that need to be taken into account to modify the inrush curve for this transformer due to the unit connection?
Question #2: The old BDD relays had instantaneous elements on them that were set at 8X tap-which really makes me question the inrush curve (see above question). I want to set the new instantaneos elements in the relay to about the same setting. Do I use the 87W1 and 87W2 CT ratios that were calculated for the differential element?
Question #3: Is there any rule of thumb for setting the timing of the 51 elements? Another engineer suggested a pickup of 125% of rating and the curve set so that at the highest current level for a fault on the 69kV bus the backups will operate in 1.5 s.
Question #4: The backup OC's will not pick up for all faults on the 69kV lines running out on the station. I wanted to use a 46 element to pick up the unbalanced faults. Is there any advice on how to set this element?
Thanks in advance
The transformer is rated at 145MVA 14.4/69 kV and connected in a delta wye configuration.
The generator is rated at 160MVA 15kV.
The two are connected in a unit configuration with two unit auxiliary transformers.
Question #1: In trying to set backup overcurrent relaying, I have found it difficult to coordinate with the inrush current curve. I have plotted the relay curves, transformer damage curve and inrush curve on a graph using Excel. The values for the inrush curve come from the Electrical Distribution System Protection book by Cooper. In reviewing relay settings for the same type of relay at another of our generating stations, I noticed that parts of the backup overcurrent curve specified for that relay lie to the left of the inrush curve for that transformer. (Similar configuration, transformer rated at 231 MVA) Are there any special considerations that need to be taken into account to modify the inrush curve for this transformer due to the unit connection?
Question #2: The old BDD relays had instantaneous elements on them that were set at 8X tap-which really makes me question the inrush curve (see above question). I want to set the new instantaneos elements in the relay to about the same setting. Do I use the 87W1 and 87W2 CT ratios that were calculated for the differential element?
Question #3: Is there any rule of thumb for setting the timing of the 51 elements? Another engineer suggested a pickup of 125% of rating and the curve set so that at the highest current level for a fault on the 69kV bus the backups will operate in 1.5 s.
Question #4: The backup OC's will not pick up for all faults on the 69kV lines running out on the station. I wanted to use a 46 element to pick up the unbalanced faults. Is there any advice on how to set this element?
Thanks in advance