"Quick Question..." is how our architects 1st posed this question. Not a quick solution. Due to the roofing they could not apply their typical detail of a metal guard rail on the roof but had it outside the perimeter and extend below the cap flashing and anchored to the side of the un-grouted masonry wall. "What Anchor should we use?" was the question. As anchors would have it, You were not going to get the strength you need from an anchor 4ft below a 200# lateral load (800#-ft moment, 2400# force needed for anchor pivoting 4" from base of bracket). So we had them add to the detail to remove and replace the top un-grouted masonry with a grouted bond beam with some continuous reinforcement. The anchor and other components I have but, I would like to justify the masonry bond beam with some design calculations. Looking for guidance on applying out-of plain lateral point load on a single course of reinforced masonry with end supports of...the wall itself ?? (no shear walls, thinking to use shear resistance at base of bond beam outside of the load pt for some reasonable length)