simboti
Mechanical
- May 24, 2003
- 15
we're a hydro-power plant with a rated output of 750Mw. one of our turbo-alternator's (Francis turbine)guide vanes (GV) have been oscillating arbitrarilly. initially we thought that this was due to the governor actuator loop and we suspected the main servo valve's position transducer and the feedback from the servomotors. however these were tested and re-adjusted as per the commissioning report. dispite these efforts the difference between the guide vane referrence and the actual guide vane opening was approximately 3%. this is unusually high. we therefore replaced the actuator (electrohydraulic convertor),the oscillations temporarily stopped, but the difference between GV ref and GV actual remained the same. we believe that there is no problem with the digital governor (PID controller). since we've checked the programe and the control parameters. how should we therefore proceed? what are the root causes of such oscillations?