Does anyone have a suggestion for a salon on what I could use for latent load per station while the hair dryer is running? Im using 1159 BTU/H for sensible heat gain. Thanks Guys
 
Replies continue below

Recommended for you

Depends on if they are using SOUL GLOW or not. I hear that stuff is pretty latent.
 
I figured each hair dryer is about 1700W, and they will run for about 12 minutes per hour each. 12mins/60min =.2 so 1700W x .2 hours = 340 watts x # of stations = my sensible heat load for the hair dryers. I didnt think it was reasonable to figure that all the hair dryers were running continuously all day at each station. I do think it is reasonable to figure that within one hour, each station could run their hair dryer for 12 mins. Opinion?
 
Your guess for sensible load sounds good to me. I might figure evaporating a couple ounces of water during that 12-minute time period too, or maybe four? I haven't see any recommended values anywhere.

I'd specify some de-stink-i-fyers as well, to cover myself.




Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Your estimate sounds in line with the WAG I use - 3w/sf lights & 3w/sf misc. heat.

DRWeig (Electrical)
9 Dec 11 17:05
Your guess for sensible load sounds good to me. I might figure evaporating a couple ounces of water during that 12-minute time period too, or maybe four? I haven't see any recommended values anywhere.

I'd specify some de-stink-i-fyers as well, to cover myself.

Good one!!! I follow the same practice! I specify an ion generator (Bio-Climatic is one) on the discharge side of the air handler. Even had a client request the same be installed on the exhaust system serving the space to eliminate odors from a sidewall louver discharging to the exteriore.