- Apr 1, 2015
- 2
I am looking for suggestions to solve a condenser motor problem in an air cooled chiller. The unit has 12 condenser fan motors – all with a common air intake. Motors are chronically failing – after forensic inspection of a couple units, we have determined electrical grounding after bearing failure. We also see a design flaw with the unit – there is a common air intake without baffling between motors. Motors that aren’t in use rotate backwards, and are under stress when called to start.
The manufacturer has addressed this flaw with proper baffling in newer models, but there is no retrofit kit for this older chiller. Any suggestions to halt reverse spin? thanks.