I have two motels built with Autoclaved Aerated Concrete with sprinklers per NFPA #13R.
These hotels are the first structure of their type in Georgia.
I was concerned about hanger attachments so I visited the factory where I was presented with a list of "approved" hanger materials but they all utilized plastic inserts with maximum weights being 150 lbs. The only exception was you drilled through the concrete plank, countersunk a hole at the top then secure the rod using double nuts and washers. As the building has a standpipe I utilized this method for hanging all pipe > 2".
Explaining the problem the shop foreman and I experimented using Sammy screws. The first one we used was a concrete Sammy but it pulled out. Next I installed a 3" wood Sammy and, properly installed, it worked just great. After installing a 3" wood Sammy we hoisted the plank up on a forklift and three of us tried to pull it out and couldn't. Hanging weight was >650 lbs and trying our best to make the hanger fail all we succeeded in doing was deforming the band hanger.
Not exactly an engineering study I was satisfied the hanger would be adequate as long as our guys installed it correctly ie don't bottom the hanger out.
The first foreman we sent on the job thought it was better to use concrete Sammy's without talking to me about it. Not having the proper tool to install he used a regular ratchet, over spun the Sammy resulting in a number of them pulling out. I corrected the situation, changed the hangers to the 3" wood Sammy, installed over 700 and not a single one pulled out.
Word got out to the project engineer about the first hangers pulling out and now I have a problem. Explained the situation, that the first hangers were for concrete and improperly installed but he's not liking any of it now. The only alternative is replace all the hangers with rod drilled through the plank and double nutted.
I see the engineers point, the wood Sammy's are listed for wood, not Aerated Concrete.
Stuff cuts like butter, you use wood saws and drillers for holes and it takes about 30 seconds to drill so it isn't the end of the world if we have to do this. I figure it will take three guys a week so it isn't like I am trapped with nowhere to go.
I take it demonstrating the hanger is capable of holding 5 times it weight (mostly 1" CPVC) plus 250 lbs is not acceptable?
Thoughts from PE types would be most appreciated.
Thanks.
These hotels are the first structure of their type in Georgia.
I was concerned about hanger attachments so I visited the factory where I was presented with a list of "approved" hanger materials but they all utilized plastic inserts with maximum weights being 150 lbs. The only exception was you drilled through the concrete plank, countersunk a hole at the top then secure the rod using double nuts and washers. As the building has a standpipe I utilized this method for hanging all pipe > 2".
Explaining the problem the shop foreman and I experimented using Sammy screws. The first one we used was a concrete Sammy but it pulled out. Next I installed a 3" wood Sammy and, properly installed, it worked just great. After installing a 3" wood Sammy we hoisted the plank up on a forklift and three of us tried to pull it out and couldn't. Hanging weight was >650 lbs and trying our best to make the hanger fail all we succeeded in doing was deforming the band hanger.
Not exactly an engineering study I was satisfied the hanger would be adequate as long as our guys installed it correctly ie don't bottom the hanger out.
The first foreman we sent on the job thought it was better to use concrete Sammy's without talking to me about it. Not having the proper tool to install he used a regular ratchet, over spun the Sammy resulting in a number of them pulling out. I corrected the situation, changed the hangers to the 3" wood Sammy, installed over 700 and not a single one pulled out.
Word got out to the project engineer about the first hangers pulling out and now I have a problem. Explained the situation, that the first hangers were for concrete and improperly installed but he's not liking any of it now. The only alternative is replace all the hangers with rod drilled through the plank and double nutted.
I see the engineers point, the wood Sammy's are listed for wood, not Aerated Concrete.
Stuff cuts like butter, you use wood saws and drillers for holes and it takes about 30 seconds to drill so it isn't the end of the world if we have to do this. I figure it will take three guys a week so it isn't like I am trapped with nowhere to go.
I take it demonstrating the hanger is capable of holding 5 times it weight (mostly 1" CPVC) plus 250 lbs is not acceptable?
Thoughts from PE types would be most appreciated.