electrician1
Electrical
- Aug 29, 2006
- 18
Working on offshore installation and we have our own power plant.
There is SCR power distribution for big dc motors and various equipment
During the last 3 months 6 computers have burned.They were all the same type and
were connected trough the same type of ups.diagnostic-mother board burned
I measured voltage supplied to computers
noticed that with SCR off (all DC motors stopped) voltage supplied to computers
looks ok and stable- THDr,THDf around 1.47% K factor=1.27 but during the operation, voltage is unstable with
increased 5th harmonic
THD factor increases to 11.90% , K factor=13.1 and computer power supply just follows voltage fluctuation on line and distribute unstable voltage to motherboard.
I read somewhere that THD factor should not be higher than 5% is that some rule or it depends about
power plant configuration and power distribution.
There is no any problem with other electronic equipment.May be will help if we just put power conditioners for all computers?
Thanks
There is SCR power distribution for big dc motors and various equipment
During the last 3 months 6 computers have burned.They were all the same type and
were connected trough the same type of ups.diagnostic-mother board burned
I measured voltage supplied to computers
noticed that with SCR off (all DC motors stopped) voltage supplied to computers
looks ok and stable- THDr,THDf around 1.47% K factor=1.27 but during the operation, voltage is unstable with
increased 5th harmonic
THD factor increases to 11.90% , K factor=13.1 and computer power supply just follows voltage fluctuation on line and distribute unstable voltage to motherboard.
I read somewhere that THD factor should not be higher than 5% is that some rule or it depends about
power plant configuration and power distribution.
There is no any problem with other electronic equipment.May be will help if we just put power conditioners for all computers?
Thanks