Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Harmonics Spectrum Analyzer

Status
Not open for further replies.

shkim2000

Electrical
Oct 12, 2004
59
In order to verify THD 5% at the power network which is 690V 3 phase, I am going to measure THD. Can you tell me Harmonics Analyzer Manufacture and Model you can recommend and what should be conseration into selection of analyzer ?
 
Replies continue below

Recommended for you

Voltech's PM3000 could connect directly to the system under test: depending on the current level you are measuring you might need to use CTs. It will measure current and voltage THD, and give you harmonic power too.

If you use an isolating transducer with good bandwidth you could use any of the numerous spectrum analysers from the usual manufacturers.


----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!
 
Try the Fluke 430 Series Three-Phase Power Quality Analyzers. I haven't used it but we did use the Fluke 41 which was an older single phase version.
 