we have two transformers supplying our facility these being 11kv to 415v rated at 2.5mva.
Both are oil cooled and one is running roughly 10 deg hotter than the other.
doing a check on the harmonics we got the following -
cool transformer hot transformer
THD 22.70% 74.60%
THD EVEN 2.50% 5.90%
THD ODD 22.80% 75.40%
K FACTOR 5.3 11.3
C FACTOR 1.9 1.9
further checks reveal that the I4 values are way different
20.79% against 73.42%.
Looking for advice and recommendations as to how to go on from here. I take it that this isnt a good position to be in.