Header arrangement for 2 antifreeze zones

Status
Not open for further replies.

Moshersprink

Mechanical
Feb 12, 2011
2
Hi everyone, my first post here and want to thank everybody for the interesting Q&A on this site. I've been reading for a while :)

I'm looking at a situation where 2 small antifreeze zones are required (NFPA 13 occupancy). Each zone will be <20 Gallons. To reduce costs I'm wondering if it is possible to have the 2 zone control stations downstream of 1 RP backflow assembly?

Thanks!
 
Replies continue below

Recommended for you

What is your question exactly?

If you are asking whether one backflow assembly can supply two control valves, there is no reason why not.
 
Thanks. Seems like a dumb question but just wanted to be sure. I don't have a lot of experience with antifreeze systems and for some reason thought a separate RP backflow assembly might be required for each zone.
 