Heat Collectors/Baffels Sizing

Status
Not open for further replies.

AdamMurray

Mechanical
Dec 23, 2003
18
0
0
CA
Just wondering if anyone could point me in the right direction. I am looking for NFPA or ULC references for sizing and placement of heat collectors for sprinkler heads and heat detectors.

The heads and /or deflectors would be located approx. 20 feet from roof deck. Are local application protecting equipment (pre-action system).

 
Replies continue below

Recommended for you

NFPA 13 which governs the installation of fire sprinkler systems does NOT address heat collectors. Sprinklers are to be located within 12" of the roof deck (with a few exceptions). The idea of heat collectors has been around for probably as long as sprinklers have been around.

I truly doubt you will find anywhere that talks about sizing or placement of a heat collector.

Things I have seen around are standard 12" pie pans....before you do anything, get the local AHJs to sign off, because it is beyond the scope of NFPA 13.

 