I am trying to work out heat losses in panel and want to include for cabling. 60Hz 3phase system
Am I correct in saying formula is i2R where R is ac resistance of cabling.
We have 9off 95mm.sq conductors per phase and there is approx 300mm between terminations and the sealed deckhead through which they transit into panel. So total cable length is 9 x 3 x 300m = 8.1m
AC resistance of cable is given as 0.23ohms/km, so total resistance is (0.23 x 8.1)/1000 = 1.863mohms.
Current in circuit is 1100A.
That gives about 2.15kW. That seemed high to me have I simplified this too much ?
The panel is IP67, with surface area of 5m2, there are no cooling fans or inlet grills. There is busbar and circuit breakers inside. I am trying to work out the watts dissipated in the panel and whether the surface area (mild steel) can remove the heat without causing excessive rise. This calc alone seems to blow it out of the water suggesting we have an oven from the cabling alone! this is before I even consider busbar losses and circuit breaker pole losses. Hence I'd like to clarify my calcs.
(apologies for the metric units!)
Am I correct in saying formula is i2R where R is ac resistance of cabling.
We have 9off 95mm.sq conductors per phase and there is approx 300mm between terminations and the sealed deckhead through which they transit into panel. So total cable length is 9 x 3 x 300m = 8.1m
AC resistance of cable is given as 0.23ohms/km, so total resistance is (0.23 x 8.1)/1000 = 1.863mohms.
Current in circuit is 1100A.
That gives about 2.15kW. That seemed high to me have I simplified this too much ?
The panel is IP67, with surface area of 5m2, there are no cooling fans or inlet grills. There is busbar and circuit breakers inside. I am trying to work out the watts dissipated in the panel and whether the surface area (mild steel) can remove the heat without causing excessive rise. This calc alone seems to blow it out of the water suggesting we have an oven from the cabling alone! this is before I even consider busbar losses and circuit breaker pole losses. Hence I'd like to clarify my calcs.
(apologies for the metric units!)