Jim:
I'm a mechanical so please bear with me!
Let's see 150kVA =~ 150,000 whatchamacallits = (about) 150kW.
1 kW = 3,412 BTUH (the Brits don't even use BTUs!!)
So 150 kW = 150 x 3,412 = 511,800 BTUH. Divide taht by 12,000BTUH/ton and youhave a heat gain of a whopping 42.6 tons! This is a whole lot of heat to pump outside if you consider that mechanical cooling in this size range can cost about $800/ton. Better to just ventilate the closet with outside air ... unless you're in the Saharah; but check the max allowable op temps of your trannys.