I, once again, want to bring up the issue of heat load of motors to your kind notice. I have been observing the designers using the following equations for heat load of motors, that confused me since I started learning about HVAC.
Motor and driven machine inside control space - HPx2545/eff.
Motor out driven machine in - HPx2545
Motor in driven machine out - HPx2545x(1-eff)/eff
Now coming to my question, if I have a chiller placed inside a controlled space (may not be within the same space which is conditioned by this particular chiller), what will be the heat load due to this chiller to the controlled space?
I am sincerely awaiting some discussion on this topic.