heat loads.

Status
Not open for further replies.

popibear99

Marine/Ocean
Dec 16, 2012
1
thread403-50052

Found this to be a good thread. I'm stuck with calculating heat load, with answer expressed in CFM. What would be the formula if I had 5,000 gal/hr of cooling water with a 10 degree delta T?
 
Replies continue below

Recommended for you

mass flow * specific heat * delta temperature

TTFN
faq731-376
7ofakss
 
IRstuff's answer will give you BTU/hr. For water in HVAC applications, a simplification is

500*GPM*(delta-T)

To convert to air flow in CFM, you'll need to know the difference in supply air temperature and space temperature, plus the load. Not enough info given.

Best to you,

Goober Dave