w2jo
Electrical
- Jul 22, 2007
- 29
My job is to interface various HVAC and other equipment to Building Automation Systems. I have just (about) completed the interface of a Carrier Infinity Heat Pump to a standard Building Automation Controller. This involved complete replacement of the existing Infinity HP controller so as to allow detailed control and monitoring of the HP by the building automation system.
Every thing is finished and working fine, but I am thinking that the DEFROST CYCLE for the HP is more complex than it needs to be. Maybe someone can educate me.
What I implemented (in accord with Carrier's Manual) is:
1) Set minimum defrost interval to 30 minutes at power up.
2) If minimum defrost interval timer has expired AND OCT (outside expansion coil exit temp) is less than 32F for 5 minutes, then initiate defrost cycle.
3) If the prior defrost cycle took less than 3 minutes (for OCT to reach 65F which signifies "defrost complete", set minimum defrost interval to 90 minutes. If it took 3>6 minutes set next interval to 60 minutes. If more than 6 minutes set next interval to 30 minutes. (This 30/60/90 selection is the continuous running time UNTIL the next defrost is ALLOWED to occur. The defrost cycle is not run unless #2 above is satisfied.
I have noticed that the typical OCT coil exit temp to Outside Air temp when running in HIGH HEAT MODE is about 8 degrees F after stabilizing for 5 minutes. I also have noticed that the OCT temp difference to outside air temp increases as the outside coil ices up as one would expect. When the coil to Outside Air temp is about 12F, the coil is getting "fuzzy" with ice.
It seems to me that if I keep a long term trend of the delta-T (temp difference, Outside Coil to Outside Air in HEAT MODE) and use that as a baseline, I should enter the defrost cycle about when the delta-T gets to 12F or so.
Is there anything I am missing with the above protocol?
Also, Is there a good rule of thumb criteria for a temperature below which a heat pump should not be run? Some have told me 40F, others 37F and others 32F. It seems to me that as long as the compressor AMPS are within specs and the defrost cycle is working the machine should be capable of operating independent of any set minimum temperature.
My criteria for terminating heat pump operation might be if the defrost cycle took more than (say) 20% of the "between defrost cycle" HP running time then stop using the heat pump until the temperature rises. Anyone have any thoughts here?
Many thanks for your helpul comment.
Joe
Every thing is finished and working fine, but I am thinking that the DEFROST CYCLE for the HP is more complex than it needs to be. Maybe someone can educate me.
What I implemented (in accord with Carrier's Manual) is:
1) Set minimum defrost interval to 30 minutes at power up.
2) If minimum defrost interval timer has expired AND OCT (outside expansion coil exit temp) is less than 32F for 5 minutes, then initiate defrost cycle.
3) If the prior defrost cycle took less than 3 minutes (for OCT to reach 65F which signifies "defrost complete", set minimum defrost interval to 90 minutes. If it took 3>6 minutes set next interval to 60 minutes. If more than 6 minutes set next interval to 30 minutes. (This 30/60/90 selection is the continuous running time UNTIL the next defrost is ALLOWED to occur. The defrost cycle is not run unless #2 above is satisfied.
I have noticed that the typical OCT coil exit temp to Outside Air temp when running in HIGH HEAT MODE is about 8 degrees F after stabilizing for 5 minutes. I also have noticed that the OCT temp difference to outside air temp increases as the outside coil ices up as one would expect. When the coil to Outside Air temp is about 12F, the coil is getting "fuzzy" with ice.
It seems to me that if I keep a long term trend of the delta-T (temp difference, Outside Coil to Outside Air in HEAT MODE) and use that as a baseline, I should enter the defrost cycle about when the delta-T gets to 12F or so.
Is there anything I am missing with the above protocol?
Also, Is there a good rule of thumb criteria for a temperature below which a heat pump should not be run? Some have told me 40F, others 37F and others 32F. It seems to me that as long as the compressor AMPS are within specs and the defrost cycle is working the machine should be capable of operating independent of any set minimum temperature.
My criteria for terminating heat pump operation might be if the defrost cycle took more than (say) 20% of the "between defrost cycle" HP running time then stop using the heat pump until the temperature rises. Anyone have any thoughts here?
Many thanks for your helpul comment.
Joe