I have just reviewed a TAB report and 35 McQuay heat pumps indicated supply air temperatures ranging from 6 to 8 degrees C in the air conditioning mode. This cannot be correct and is too cold. I am wondering if excessive water flow through the heat pumps would lower head pressure sufficiently to reduce suction pressure and ultimately supply air temperature.
I haven't yet ruled out mis-calibration of the DDC sensors, although re-caibration of sensors was a part of the project scope.
Water flow in the loop was not measured... although EWT=27.2C and LWT=32C so delta T seems in the correct range.
Airflows across the coil were 500 to 600 L/s after air balance
Suggestions for further troubleshooting??
Tom
I haven't yet ruled out mis-calibration of the DDC sensors, although re-caibration of sensors was a part of the project scope.
Water flow in the loop was not measured... although EWT=27.2C and LWT=32C so delta T seems in the correct range.
Airflows across the coil were 500 to 600 L/s after air balance
Suggestions for further troubleshooting??