moideen
Mechanical
- May 9, 2006
- 360
I have an existing 2 no swimming pool heat pump, both are locally manufactured , so there is not any datasheet available to know the design flow rate. Manufacture told and compressor datasheet says that both rated with 20 ton (total heating capacity 200 kw). the flow rate can assume 50 gpm per unit( ton *2.4 gpm)The issues related with the coincide operation of pool filter pump. The Heat pump hasn’t dedicated pump, but using the same flow of filter pump.
The filter pump’s flow rate is 300 gpm which circulate through the heat pump, for heat pump its maximum flow 50 gpm(11m3h) only per unit. As per the present scenario circulates 300 gpm(68m3h) through HX. The Situation goes to worsen that high pressure water is bleeding from pipe fittings when close the valve of any heat pump. I attached the hand sketch of pipe’s schematic.
I want to plan open the bypass valve completely and fit a PRV on the line into the heat pump, and two picv for individual circuit of HX. helpful comment is appreciated. Thanks
The filter pump’s flow rate is 300 gpm which circulate through the heat pump, for heat pump its maximum flow 50 gpm(11m3h) only per unit. As per the present scenario circulates 300 gpm(68m3h) through HX. The Situation goes to worsen that high pressure water is bleeding from pipe fittings when close the valve of any heat pump. I attached the hand sketch of pipe’s schematic.
I want to plan open the bypass valve completely and fit a PRV on the line into the heat pump, and two picv for individual circuit of HX. helpful comment is appreciated. Thanks