Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Heat Rejected to room by VSD's

Status
Not open for further replies.

RRD

Mechanical
Jun 15, 2003
2
I am looking at providing A/C to a switchroom which includes VSD of varying manufacture.

Aside from asking the supplier for possible information which is a little sketchy at times (sales staff who read catalogue data back to you but can provide no further insight), does anyone have a rule of thumb for determining the heat rejected to the room.

I seem to be able to obtain cooling airflow rates for some of the VSD's but I cannot obtain a reference temperature rise in order to determine the heat rejected.

I do not want to significantly over size the unit due to the loads off the VSD's.

Any help would be appreciated.
 
Replies continue below

Recommended for you

Check you catalog data; most that I have provide tables showing watts lost vs. min/max speeds... convert to BTU's per hour for determining cooling loads..
 
Also, there is a rule of thumb: use 2 to 6% of the (ASD)drives kVA rating (I have not used this nor have I compared it to the manufacturers' data)
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor