Does anyone have a usefull formula for estimating the heat losses in medium voltage fuses based on loading? We are doing heat runs on some equipment and the hottest parts are the fuses and clips. With a 1200kW 11kV load, we are seeing 22kW in total heat loss, of which only 4kW can be accounted for in all the other components combined. That means we are seeing 18kW in losses through the fuses and holders. That is 1-1/2% of the total load! I think there is a problem with the clips, but I don't know what to estimate from the fuses to help prove my point. The fuse mfgr. is slow to respond, so I was hoping someone here already knows.