Hi,
I have a problem with the levels in the LP and HP hetaers of our solar plant. When there is a high level on the LP heaters the turbine closes its extraction and it trips the turbine. The heaters have 3 wave guided level transmitters from VEGA. These High levels are usually sudden peaks and never remain as high.
I was thinking to configure the transmitters with a damping so that theses peaks are not detected, I am not sure and cant really prove that they are real condensate peaks. If they are and I ignore these with a damping I might be putting water in the Turbine, but If they are not, I am tripping the turbine for the sake of it.
1. How can I determine if these peaks are real, having someone by the local level indicator to contrast this is hard since these are not frequent or slow).
2. Could It be to risky to damp the signals?
I have a problem with the levels in the LP and HP hetaers of our solar plant. When there is a high level on the LP heaters the turbine closes its extraction and it trips the turbine. The heaters have 3 wave guided level transmitters from VEGA. These High levels are usually sudden peaks and never remain as high.
I was thinking to configure the transmitters with a damping so that theses peaks are not detected, I am not sure and cant really prove that they are real condensate peaks. If they are and I ignore these with a damping I might be putting water in the Turbine, but If they are not, I am tripping the turbine for the sake of it.
1. How can I determine if these peaks are real, having someone by the local level indicator to contrast this is hard since these are not frequent or slow).
2. Could It be to risky to damp the signals?