Hello all
I have a question:
I am traying to select an AHU ( hot water for heating, DX for cooling) for an application.
For the cooling side th unit is ok
but, for the heating side the capacity of the coil with the nominal water flow mentioned in the catalog is much higher than my requirment.
example: my requirment is 130000 BTU/hr
equipment coil has capacity of 200000 BTU/hr. at 20GPM flow rate
The catalog didn't give the BTU output at a different flow rate.
What would happen(beside the 3 way control valve will cycle on/off too much.)
if I go with 20GPM and size the pipes with keeping the unit fan in [On] mode all the time?
any suggestions
Thank you