Hi
I need some help checking my line of reasoning, as it seems we can not get to a decision at work.
I am pouring a column, the column is inclined at an angle (Say 52.2 deg), and it will be poured in two lifts (No more than 13ft in vertical).
The columns are formed (Not concerned about this), and the scaffolding system is generic 10K or other tower like system.
The problem starts on the second pour, to get the horizontal loads due to the inclined concrete. This horizontal loads will be transferred to the Forming/ Struts & scaffolding system, and the bracing/ lacing/ tie down will be designed based on them.
See attached pdf.
1. First, the previously poured lift, concrete has already hardened, and it doesn't exert any pressure over the forms. Only its weight, which acts vertically, and needs to be adjusted for the inclination. (vertical distance "t" * Ɣc (150 pcf) * cos(θ)^2 * influence (2 supports))
2. Second, freshly poured concrete, the final pressure on the forms will be due to the weight (vertical) & the horizontal pressure (Fixed at a max. of 600 psf or 4ft of liquid head), all adjusted for the angle of inclination of the struts. For weight same as point 1, for pressure Pmax. (600 psf) * sin(θ)^2 * influence.
All the weights & pressures being adjusted by the inclination, I can treat it all as a beam, and find reactions, with reactions and angle of inclination, I can find Horizontal & Vertical (Taken by tower legs) loads.
Can someone confirm or correct me?
I need some help checking my line of reasoning, as it seems we can not get to a decision at work.
I am pouring a column, the column is inclined at an angle (Say 52.2 deg), and it will be poured in two lifts (No more than 13ft in vertical).
The columns are formed (Not concerned about this), and the scaffolding system is generic 10K or other tower like system.
The problem starts on the second pour, to get the horizontal loads due to the inclined concrete. This horizontal loads will be transferred to the Forming/ Struts & scaffolding system, and the bracing/ lacing/ tie down will be designed based on them.
See attached pdf.
1. First, the previously poured lift, concrete has already hardened, and it doesn't exert any pressure over the forms. Only its weight, which acts vertically, and needs to be adjusted for the inclination. (vertical distance "t" * Ɣc (150 pcf) * cos(θ)^2 * influence (2 supports))
2. Second, freshly poured concrete, the final pressure on the forms will be due to the weight (vertical) & the horizontal pressure (Fixed at a max. of 600 psf or 4ft of liquid head), all adjusted for the angle of inclination of the struts. For weight same as point 1, for pressure Pmax. (600 psf) * sin(θ)^2 * influence.
All the weights & pressures being adjusted by the inclination, I can treat it all as a beam, and find reactions, with reactions and angle of inclination, I can find Horizontal & Vertical (Taken by tower legs) loads.
Can someone confirm or correct me?