Tomas7
Mechanical
- Aug 28, 2020
- 2
Hi,
I am a Development Manager working in the energy industry in Australia. I want to learn more about what to do when there is a network issue or in this case work out what size of PV plant we can install. The company that I work for proposed a 10 MWac solar PV farm and the network company who performed the preliminary assessment of system strength came to the conclusion that the Available Fault levels became negative and the short circuit calculation indicates a shortfall. I have attached the preliminary assessment report and our selected Inverter information so that you can get all the information that I have. I have covered sensitive information because this is a live project.
What I would like to work out without using Digsilent Powerfactory or similar software is approximately what size PV plant we can connect without a shortfall in Available Fault levels at our connection point. [highlight #FCE94F]Is that possible?[/highlight] I just need an approximate figure.
The screening technique the network used was the Minimum Short Circuit Ratio method, also known as MSCR. They used the nameplate inverter capacity for this exercise which are listed in the attached report.
Information about our proposed solar PV plant. We intended to connect two different 4.95 MW solar plants to two different bus bars, one at 11 kV and the other at 22 kV, each plant was going to be 4.95 MW real power export capacity and 9.8 MVA of inverter capacity for reactive power support. There is another bigger solar farm upstream to our connection point which the network has included in their assessment, it is a 217.25 MVA solar plant.
Here is a link to the single line diagram for our two connections.
I would be happy to offer a consultancy fee if you like.
Appreciate your help thanks,
Tomas
I am a Development Manager working in the energy industry in Australia. I want to learn more about what to do when there is a network issue or in this case work out what size of PV plant we can install. The company that I work for proposed a 10 MWac solar PV farm and the network company who performed the preliminary assessment of system strength came to the conclusion that the Available Fault levels became negative and the short circuit calculation indicates a shortfall. I have attached the preliminary assessment report and our selected Inverter information so that you can get all the information that I have. I have covered sensitive information because this is a live project.
What I would like to work out without using Digsilent Powerfactory or similar software is approximately what size PV plant we can connect without a shortfall in Available Fault levels at our connection point. [highlight #FCE94F]Is that possible?[/highlight] I just need an approximate figure.
The screening technique the network used was the Minimum Short Circuit Ratio method, also known as MSCR. They used the nameplate inverter capacity for this exercise which are listed in the attached report.
Information about our proposed solar PV plant. We intended to connect two different 4.95 MW solar plants to two different bus bars, one at 11 kV and the other at 22 kV, each plant was going to be 4.95 MW real power export capacity and 9.8 MVA of inverter capacity for reactive power support. There is another bigger solar farm upstream to our connection point which the network has included in their assessment, it is a 217.25 MVA solar plant.
Here is a link to the single line diagram for our two connections.
I would be happy to offer a consultancy fee if you like.
Appreciate your help thanks,
Tomas