Langless28
Mechanical
- Dec 29, 2014
- 14
I have a machine that is single phase 240vac operation. Power in is L1,L2, and the grounding conductor. I would like to step down the voltage to 120vac so i can power a single convenience outlet meant to only power a small ionizing fan that is to be used on the unit.
The control transformer is 240/440 primary with 120vac secondary coil (single coil). From what i have read is you are supposed to obtain the grounded (neutral) conductor by bonding X2 of the secondary to ground. My questions are as follows:
1. Is this the correct method? From what i have always understood was that the grounded and grounding conductors are only ever tied together at the main panel.
2. If it is how you do it, can it be bonded directly at the place of installation? does it need a dedicated groundING conductor all the way to the main power entry of the machine?
3. Does it need a neutral? can the voltage be "floating". If so, what are the benefits and negatives of this?
The control transformer is 240/440 primary with 120vac secondary coil (single coil). From what i have read is you are supposed to obtain the grounded (neutral) conductor by bonding X2 of the secondary to ground. My questions are as follows:
1. Is this the correct method? From what i have always understood was that the grounded and grounding conductors are only ever tied together at the main panel.
2. If it is how you do it, can it be bonded directly at the place of installation? does it need a dedicated groundING conductor all the way to the main power entry of the machine?
3. Does it need a neutral? can the voltage be "floating". If so, what are the benefits and negatives of this?