haze10
Electrical
- Jan 13, 2006
- 81
One of the relay on our main circuit breaker is a GE#12ICR53A1A, Ansi#47, Phase Sequence and UnderVoltage Relay.
I've read the manual but still not sure of how it works. This is from the manual:
The Type ICR relays are used to protect AC machines from undervoltage and when
starting from open phase or reverse phase sequence. They will function to stop the
machine if the voltage across the relay terminals falls below a predetermined
value. Usually these relays will not disconnect a running motor if one phase of
the supply is open-circuited because the motor will supply three-phase potential to
the relay even with one phase disconnected from the source. The Type ICR relay
are also used for automatic throw over schemes where it is desired to check the
presence of three-phase voltage of correct phase sequence.
The 47 relay is on 4.16KV MCB that feeds a line up of 4.16KV feeder breakers, that in turn provide cables underground to building transformers. The original purpose of this relay (I am told) was to protect the motors on site from phase loss, and/or, reverse phase rotation. There is a time delay time on the relay set to 3 seconds.
Questions:
Phase Sequence? Does this phase rotation, in the sense that if I presently have clockwise rotation (ABC), and do to some external mistake the switchgear was supplied with counterclockwise rotation (ACB) the relay would open the MCB? Does the 3 second delay engage on this function. 3 seconds of rotating motors in the opposite direction could do a lot of damage.
Undervoltage Relay? Is this the 'phase lost' part of the relay? I can understand the 3 second timer being here.
Total Loss of Power? All the protective relays are supplied from batteries. So if we have a utility outage, loss all three phases simultaneously, is the 47 relay going to trip open the MCB? I would prefer that it doesn't, as then we could automatically recover once power was restored without suiting up an electrician to close the MCB, but not sure if that is possible. Does the 47 relay take losing all three phases the same as losing one phase?
Any advice you can provide is appreciated.
haze10
I've read the manual but still not sure of how it works. This is from the manual:
The Type ICR relays are used to protect AC machines from undervoltage and when
starting from open phase or reverse phase sequence. They will function to stop the
machine if the voltage across the relay terminals falls below a predetermined
value. Usually these relays will not disconnect a running motor if one phase of
the supply is open-circuited because the motor will supply three-phase potential to
the relay even with one phase disconnected from the source. The Type ICR relay
are also used for automatic throw over schemes where it is desired to check the
presence of three-phase voltage of correct phase sequence.
The 47 relay is on 4.16KV MCB that feeds a line up of 4.16KV feeder breakers, that in turn provide cables underground to building transformers. The original purpose of this relay (I am told) was to protect the motors on site from phase loss, and/or, reverse phase rotation. There is a time delay time on the relay set to 3 seconds.
Questions:
Phase Sequence? Does this phase rotation, in the sense that if I presently have clockwise rotation (ABC), and do to some external mistake the switchgear was supplied with counterclockwise rotation (ACB) the relay would open the MCB? Does the 3 second delay engage on this function. 3 seconds of rotating motors in the opposite direction could do a lot of damage.
Undervoltage Relay? Is this the 'phase lost' part of the relay? I can understand the 3 second timer being here.
Total Loss of Power? All the protective relays are supplied from batteries. So if we have a utility outage, loss all three phases simultaneously, is the 47 relay going to trip open the MCB? I would prefer that it doesn't, as then we could automatically recover once power was restored without suiting up an electrician to close the MCB, but not sure if that is possible. Does the 47 relay take losing all three phases the same as losing one phase?
Any advice you can provide is appreciated.
haze10