Per ANSI/FCI70-2-1991 Class IV shut-off described as 0.01% of rated valve capacity. Test procedure A.
Valve capacity described as “the quantity of test fluid (air or water) that would pass through the valve at rated travel under the stated pressure conditions as determined by the appropriate equations and manufacturer’s ratings.
Test Procedure A:
5.1.2 Pressure of test medium shall be 3-4 bar (45-60 psig) or the maximum operating differential pressure whichever is less
My question is:
If only the cv value of the valve and the Class of the shut-off known. How I can test and know if the vavle is Class IV shutoff.
Should I test the valve with 45-60 psi water. If the seat leakage is less then 0.01%of the cv value, does it meet the standard. Or do I need to convert the cv value to "rated valve capacity", ifso how do i do that.
Thanks for your help