Can anyone help me on this one: How to coordinate the CB protecting a low-voltage dry-type transformer serving motors.
The overview of the system is this: 2 grids of MV utility = 34.5kV each; 2 nos. of unit substation transformers feeding each end of a double-ended LV switchgear = 3000kVA, 34.5kV-0.48kV/0.277kV, 5.75%Z each; the double-ended switchgear (480V/277V) with a branch circuit breaker feeding the 1000kVA, 480V-208V/120V 3-phase dry-type transformer approximately 75 meters away.
At the primary side of the said dry-type transformer, I provided a circuit breaker. However, I am a bit lost in coordinating:
(1)the branch circuit breaker of the switchgear, where the feed comes from,
(2)the circuit breaker for the primary of the dry-type transformer and
(3)the circuit breakers of the MCC.
This dry-type transformer serves an MCC with 3-phase motors at 208V (mostly pumps - the owner purchased pumps rated at 208V instead of 480V).
Shall these pump motors still contribute to the short-circuit current to be considered in the switchgear? If so, how do I reflect the possible contributions of these motors upstream to the mains?
Your immediate response shall be highly appreciated. Thanks and more power to you all.
The overview of the system is this: 2 grids of MV utility = 34.5kV each; 2 nos. of unit substation transformers feeding each end of a double-ended LV switchgear = 3000kVA, 34.5kV-0.48kV/0.277kV, 5.75%Z each; the double-ended switchgear (480V/277V) with a branch circuit breaker feeding the 1000kVA, 480V-208V/120V 3-phase dry-type transformer approximately 75 meters away.
At the primary side of the said dry-type transformer, I provided a circuit breaker. However, I am a bit lost in coordinating:
(1)the branch circuit breaker of the switchgear, where the feed comes from,
(2)the circuit breaker for the primary of the dry-type transformer and
(3)the circuit breakers of the MCC.
This dry-type transformer serves an MCC with 3-phase motors at 208V (mostly pumps - the owner purchased pumps rated at 208V instead of 480V).
Shall these pump motors still contribute to the short-circuit current to be considered in the switchgear? If so, how do I reflect the possible contributions of these motors upstream to the mains?
Your immediate response shall be highly appreciated. Thanks and more power to you all.