I'm looking at the existing system with three undervoltage relays connected to the three 12.47kV feeders into the Plant
... there's a 12470/240-120V CPT on each one.
The test data shows:
Bus #1: PU at 109V and drops out at 105V.
109V/120V = 90% voltage, on the primary side this would be 11,223V
Bus #2: Another 12kV bus has the same relay and it says the Instantaneous function is set to DO = 55.91V and PU = 55.25V, and the time delay function is disabled. 55.91V/120V = 47% voltage. On the primary side 12,470V * .47 = 5860.9V
Bus #3: Another bus has this function done by a 47 relay. With settings PU V = 100 and DO V = 80V and an operating time of .0254 seconds
100/120 = .83, 80/120 = 0.67, => 10,350V and 8354V
Why is there such differences in all these settings ? Also, what is the difference between the PU value and the DO V ?