sparkview
Electrical
- Nov 12, 2015
- 59
Dear all,
We are currently replacing two 60kV feeder cables and would like if someone could help with the new over current relay settings and selectivity. The single line diagram with cable specs are attached. Furthermore, old cable and relay settings details are found below. In advance many thanks for your cooperation and support and if additional information is required please advise.
Old cable specs:
NKF XLPE CU 60kV
3/C 120 mm2
Maximum calculated ampacity: 220 Amps
Old relay settings:
IEC – Normal Inverse
I> = 0.55 Relay Amps: 2.75 Prim. Amps: 220
Time Dial (k): 0.4
I>> = 10.13 Relay Amps.: 50.65 Prim. Amps: 4052
Delay (sec): 0.35
New cable Specs:
TKF YLKrvdlwd 87/150 kV
3-1/C 400 mm2
Maximum calculated ampacity: 365 Amps
New relay settings (recommended):
IEC – Normal Inverse
I> = 1
Time dial (k factor) = 0.4
I>> = 10.13
Delay (sec): 0.35
We are currently replacing two 60kV feeder cables and would like if someone could help with the new over current relay settings and selectivity. The single line diagram with cable specs are attached. Furthermore, old cable and relay settings details are found below. In advance many thanks for your cooperation and support and if additional information is required please advise.
Old cable specs:
NKF XLPE CU 60kV
3/C 120 mm2
Maximum calculated ampacity: 220 Amps
Old relay settings:
IEC – Normal Inverse
I> = 0.55 Relay Amps: 2.75 Prim. Amps: 220
Time Dial (k): 0.4
I>> = 10.13 Relay Amps.: 50.65 Prim. Amps: 4052
Delay (sec): 0.35
New cable Specs:
TKF YLKrvdlwd 87/150 kV
3-1/C 400 mm2
Maximum calculated ampacity: 365 Amps
New relay settings (recommended):
IEC – Normal Inverse
I> = 1
Time dial (k factor) = 0.4
I>> = 10.13
Delay (sec): 0.35